Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NESC 235E and Table 235-6

Status
Not open for further replies.

reed0519

Civil/Environmental
Jan 25, 2012
7
I would like to get some clarification on whether to use phase-to-phase voltage or phase-to-ground voltage when calculating clearances described in Table 235-6 of the NESC Code. The table clearly states circuit phase-to-phase voltage in the column headers but the title references Rule 235A which states using phase-to-ground of the higher voltage circuit or the phasor difference between the conductors involved. Other clearance calculations in Rule 235 are using phase-to-ground voltage, as well as the example calculations. Where this clearance is to a grounded part of the structure I would guess (fyi, I'm a civil engineer) that the phase-to-ground voltage would be more appropriate. Can anyone offer some clarification and maybe an explanation?

Thanks!
 
Replies continue below

Recommended for you

UPDATE: It is indeed phase-to-phase, unless note 10 is referenced.
 