NETA MTS-2011, Part 7.6.1.1, Section 3.2.3 indicates that the contact resistance, in this case on a molded case circuit breaker, that in absence of manufacturer's data, the standard suggests to investigate the problem if a value deviates from adjacent poles or similar breakers by more than 50% of the lowest value. However, at what point is it considered bad enough for replacement? Generally, the techs operate the breaker 3-4 times prior to taking a final reading. However, when all three poles are reading in the micro-ohm range anyway, and there are not any tripping problems occurring, when is a breaker considered bad? Molded case circuit breakers are not intended to be worked on and usually that type of breaker is considered "a throw-away"?