Helloeverybody, I received yesterday an asincronous generator on my office, and It`s comes with the neutral cable burnst.
This generator is from an hydro unit, and the nameplate is 750 Kw, 1000 rpm, 380 V. This is the only problem, the cable that conects the star point with the terminal to ground is burnst.
On my opinion:
- Maybe we got a third harmonic problem.
- Maybe we got a severe unbalance.
There isn`t trend of the currents or some else information. This is a plant that have no so good control.
Please, could somebody tell me if there is other causes that could cause this problem, and how can I avoid it, at this moment I´m thinking about multiply for 2,5 the nominal size.
thank in advance