In a substation feeding to arc furnace transformers continuous neutral current is noticed. Transformer 80 MVA 220/33 kV Ynyn connection with a stabilising tertiary winding.. HV transformer neutral is continuously showing 6-7 A irrespective of load.Because of this to avoid tripping on charging REF relay had to be set at 20 %. What can be the reason for this neutral current on HV? How to prevent this?
The current values on HV- 24,22,25,7 A (R,Y, B,Yn)(9.5 % of rated load)
LV- 167,163,168,0.21 A
HV- 3.8,3.8,4.0,6 A
LV- 27,26,28,0.2 A