Neutral Grounding Transformer 1

Status
Not open for further replies.

kingi

Electrical
Jun 16, 2005
15
This is a solidly grounded star on the primary and open corner delta, with resistor in the delta, on the secondary grounding transformer on a 12.6 kV delta system. The transformer permits 15A 3Io current in the star ground. There are a few feeders with negligible capacitance but two of the feeders have 3-4 A capacitive current.

How do I calculate the feeder ground relay settings that will not result in sympathetic tripping (tripping of a feeder for a ground fault on another feeder)? How do I combine the capacitive charging current with the transformer 3Io current? Can I neglect the capacitive current in the setting calculations? Is there any source of information that will sufficiently discuss this problem?
 
Replies continue below

Recommended for you

Hello,

You may look at several websites from relays manufacturers, they do typically have some papers in which they discuss topics like yours.
I recommend you to visit GE and/or SEL.

Another good reference could be some books, you may take a look at: Protecive Relaying from Mr Blackburn, he typically details step by step.

 