A new 30MvA 11kv generator connected to a new abb 35MVA 11/20kv ynd11 transformer.to be synchronized with other genset in 20kv busbar.
My questions are:
1-We started the set with no load ,all phases voltages in transformer output are identical 20kv but residual voltage (read from broken delta by) is 350v(CTs polarity tested )Neutral resistor in TR start point IS OPEN and in generator star point is closed what are proper causes?
2-at no load what is the range of normal THD of voltage?
My questions are:
1-We started the set with no load ,all phases voltages in transformer output are identical 20kv but residual voltage (read from broken delta by) is 350v(CTs polarity tested )Neutral resistor in TR start point IS OPEN and in generator star point is closed what are proper causes?
2-at no load what is the range of normal THD of voltage?