Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations pierreick on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

New Flare station

Status
Not open for further replies.

Sufean Alrawe

Mechanical
Jan 25, 2020
4
Hi All
We are working to add new flare station in our plant. Our plant specializes in the production of biogas from digesters, which is then utilized by our gas turbines. The project at 90%, I noticed the new flare required 3 minuets air purge cycle prior to beginning the ignition sequence to ensure no potential explosive gas exists inside.
However, In cases where we experience a loss of gas turbines and need immediate pressure relief for the biogas, our current flare system does not require an air purge cycle and can provide relief promptly. The new flare operation(Need three minutes to start) could lead to increased pressure within the digester, potentially resulting in damage of the digesters seal. Are there any specific codes or standards that mandate the air purge for flare. Thanks in advance for your help.
 
Replies continue below

Recommended for you

Use a continuous N2 purge on the new flare gathering headers to avoid the purge sequence. If N2 is not available, use a small continuous flow of biogas, which is mostly methane ( > 96 % v/v dry basis) I presume.
 
Consult the vendor if this flare was designed to withstand a flashback. See para. A.7 API 537 and para. 5.7.6 API 521.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor