I am working on a project where a folding wall is being suspended from existing wood floor trusses. Fortunately, when the wall is open, or in the stacked position, the wall will bear on the slab-on-grade. So the worst case scenario is a single, 4' wide X 8' tall panel (weight = 192#) hanging from the floor trusses as it is being moved.
I calculated the moment and reaction at a single truss, without the panel concentrated load, and then with the concentrated load. The concentrated load adds 13 percent to the bending moment (when at midspan) or the reaction (when near the support).
I think if I suspend the wall panel track from two trusses, I can live with a 6.5 percent increase in bending moment and reaction.
But what have you done in such a situation?
DaveAtkins
I calculated the moment and reaction at a single truss, without the panel concentrated load, and then with the concentrated load. The concentrated load adds 13 percent to the bending moment (when at midspan) or the reaction (when near the support).
I think if I suspend the wall panel track from two trusses, I can live with a 6.5 percent increase in bending moment and reaction.
But what have you done in such a situation?