BridgeSmith
Structural
- May 22, 2009
- 4,964
Well, I got our the first response from our city building safety office on my proposed storage loft. (Ref: Floor live load for church storage loft Some items appear to be easily handled; others I could use some advice/guidance on to address them. I'll include the whole list of the "Response Required" for completeness:
#1 - Not familiar with what a code study is. Any guidance or examples would be appreciated.
#2 - I'm assuming since this is for a church, it would be IBC?
#3 - Use is light storage. Is their assumption correct? Where would I find occupancy use definitions?
#4 - Not sure what they're asking for here. It's basically a platform with wood joists with a steel beam supporting one side, supported from the main floor (tile on concrete SOG) by wood posts.
#5 - building does not have fire suppression.
#6 - Design load is is 100 psf. Max loading will be posted.
#7 - So I need to detail the posts?
#8, #9, #10, and #12 - These I understand, I think. Shouldn't be a problem.
#11 - This could be a problem. For several reasons I can't increase the clear height underneath. This will be a storage area also - max width 19'-3"; max depth 13'-2". If I can't keep the 6'-11" I showed (yes, apparently they can't read), this project may be DOA.
#13 - There is no plan for adding or revising the electrical in the building as part of this project. We intend to have an electrical contractor draw up a plan and submit a permit application for it at a later date.
1. No code study provided
2. Codes used (Not Given)
3. Occupancy use (Not Given) A-3 assumed
4. Construction type (Not Given)
5. Is this building Fire suppressed?
6. What is the design load for your loft.
7. Show continuous load bearing beam to the ground.
8. Dimension all spaces on the floor plan.
9. Show the length of floor joists.
10. Show the landings dimensions.
11. The minimum ceiling height of not less than 7 feet 6 inches above a finished floor required. You show 6ft 8 inches.
12. Show stair landing dimensions with handrailing dimensions.
13. Missing an electrical Plan.
#1 - Not familiar with what a code study is. Any guidance or examples would be appreciated.
#2 - I'm assuming since this is for a church, it would be IBC?
#3 - Use is light storage. Is their assumption correct? Where would I find occupancy use definitions?
#4 - Not sure what they're asking for here. It's basically a platform with wood joists with a steel beam supporting one side, supported from the main floor (tile on concrete SOG) by wood posts.
#5 - building does not have fire suppression.
#6 - Design load is is 100 psf. Max loading will be posted.
#7 - So I need to detail the posts?
#8, #9, #10, and #12 - These I understand, I think. Shouldn't be a problem.
#11 - This could be a problem. For several reasons I can't increase the clear height underneath. This will be a storage area also - max width 19'-3"; max depth 13'-2". If I can't keep the 6'-11" I showed (yes, apparently they can't read), this project may be DOA.
#13 - There is no plan for adding or revising the electrical in the building as part of this project. We intend to have an electrical contractor draw up a plan and submit a permit application for it at a later date.