RM87
- Feb 19, 2013
- 52
Hello all,
I was asked sometime ago to design a new retaining wall on one side of a garage, and the other side would keep the existing concrete wall. During demolition, the contractor discovered that the existing 12" concrete wall that was intended to remain actually had 6" of unreinforced glory to it. The solution the owner and the contractor decided was to place a new wall in front of the existing wall to avoid the necessity of temporary shoring plans, etc.
Question is: The new retaining walls will now have two separately poured slabs, both with their independent keys to combat sliding. They will be abutting one another.
Should I dowel one retaining wall into the other?
Is there a specific calculation that comes to mind that you would recommend I consider?
Additional notes to consider: There's an 8" concrete slab specified to sit above the garage - the connection between the stem of the retaining walls and the slabs will have some fixity. Plus, there will be a significant amount of concrete dead load applied to those stems as well, which have been accounted for, but as an FYI. The water in the soil is a matter of high concern.
Thanks,
Rod
If so, how deep would you suggest I dowel the rebar? A tension splice would seem to call out for something like 26" but that seems unnecessary (#5 bars @ 12" O.C. top and bottom at the toe of both retaining walls, if my memory serves me...)
Should I provide a joint instead?Is there a specific calculation that comes to mind that you would recommend I consider?
Thanks,
Rod