Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Newton-Rafson load flow for synchronous condenser bus

Status
Not open for further replies.

Tofeil

Electrical
Mar 11, 2013
25
Dear user
In the newton-rafson load flow, network buses divided by 3 group: Main bus, PV buses and PQ buses.
I want to write IEEE 14 bus load flow code. How do I consider synchronous condenser bus? The PQ bus?
Regars
 
Replies continue below

Recommended for you

For simple modelling it will be a PV bus initially. If you are given reactive power capability limits on it though, and it exceeds the limits after converging, it will have to turn into a PQ bus with Q at the positive/negative limit.
 
How much its active power (P) should be determined?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor