Hi,
What is performance for the emergency lighting in designated egress stairs? Is it 10.8lux or 108lux.
7.8.1.3* The floors and other walking
surfaces within an exit and within the
portions of the exit access and exit
discharge designated in 7.8.1.1 shall be
illuminated as follows:
a. During conditions of stair use, the
minimum illumination for new stairs
shall be at least 10 ft-candle (108 lux),
measured at the walking surfaces.
7.9 then talks about the emergency lighting which states a minimum of 10.8 lux.
What are your thoughts on this?
Thanks.