NFPA 11 and 16 (foam System)

Status
Not open for further replies.

GeorgeMech

Mechanical
Nov 8, 2011
30
I have a project (fuel storage for genset application,139 m2) that requires foam system, In this project I used the deluge system, foam-Bladder type, air aspirating system, design is 6.5 li/min/m2. but after submitting the design the consultant commented that the density should be 10.2 li./m/m2 based on the hazard occupancy and I should also calculate the foam leakage from doors,etc. So is it needed for us to calculate this foam leakage since that section is for the blower type and not for air aspirating and it the 6.5li/m/m2 is enough for this design.Thanks
 
Status
Not open for further replies.