NFPA 13 heat zones 1

Status
Not open for further replies.

kylesprinkler

Mechanical
Nov 3, 2010
2
How far away should I keep the fire sprinklers from an outdoor, surface-mounted heater? These heaters will be installed in the outdoor patio areas on a house but there is nothing in 13D that describes this particular appliance.
 
Replies continue below

Recommended for you

8.3.2.5. Nfpa 13 2002 edition also same section table

And also bump to higher temp head
 
Thanks, cdafd, I looked in NFPA 13 8.3.2.5 and that section was very helpful. My sprinklers will have to be within 7 feet of the heat source so I'll bump the sprinks up to 286 deg.
 