Hello, I'm looking to use sidewall sprinklers for a heavily sloped skylight funnel (large enough that it needs to be covered by sprinklers). The slope of the funnel walls are something close to 177:100.
This is an ordinary hazard occupancy.
In NFPA 13, 2019, section 10.3.2, they specify that sidewall sprinklers shall only be installed in:
- Light hazard occupancies with smooth, horizontal or sloped, flat ceilings
- Ordinary hazard occupancies with smooth, flat ceilings where specifically listed for such use
I'm a little confused by this wording - smooth & flat don't exactly indicate if pitch is involved. They specified "horizontal or sloped" in light hazard, but brought no mention of either in ordinary hazard. I would have expected "horizontal" to be used in ordinary hazard if that was the intent. Does anyone know how to approach this?
This is an ordinary hazard occupancy.
In NFPA 13, 2019, section 10.3.2, they specify that sidewall sprinklers shall only be installed in:
- Light hazard occupancies with smooth, horizontal or sloped, flat ceilings
- Ordinary hazard occupancies with smooth, flat ceilings where specifically listed for such use
I'm a little confused by this wording - smooth & flat don't exactly indicate if pitch is involved. They specified "horizontal or sloped" in light hazard, but brought no mention of either in ordinary hazard. I would have expected "horizontal" to be used in ordinary hazard if that was the intent. Does anyone know how to approach this?