SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,244
I'm pretty sure I am correct in my approach but I would like any input.
If the 8" loop was part of the city watermain I would not have to add any domestic water allowance as the domestic water would be fed from the 8" city main and not from the main feeding the fire sprinkler riser.
However, as you can see the loop is all private and supplies both sprinklers and domestic water.
The way I read the standard is for the 48 Unit building I would have to add 185 gpm at the 4" sprinkler connection so if my sprinklers require 60 gpm I would carry 245 gpm all the way to the 12" city watermain.
Am I correct in thinking I don't have to add the domestic water use for all three apartment buildings? And no, even if I have to I would not have 485 gallons of domestic water allowance I would simply add the total units 612+612+816 for 2,040 domestic water units which would bring me to 325 gpm for all three buildings. Add to this the 60 gpm for sprinklers and I would have a total of 385 gpm sprinkler and domestic from the point of the 4" connection to the 8" loop to the city water main.
I will probably go with the 385 gpm just to play safe and avoid any possible argument.
So how would you handle this?
Travis? I know you have run into this a lot.
Construction just started and my drawings are about 50% completed.
If the 8" loop was part of the city watermain I would not have to add any domestic water allowance as the domestic water would be fed from the 8" city main and not from the main feeding the fire sprinkler riser.
However, as you can see the loop is all private and supplies both sprinklers and domestic water.
The way I read the standard is for the 48 Unit building I would have to add 185 gpm at the 4" sprinkler connection so if my sprinklers require 60 gpm I would carry 245 gpm all the way to the 12" city watermain.
Am I correct in thinking I don't have to add the domestic water use for all three apartment buildings? And no, even if I have to I would not have 485 gallons of domestic water allowance I would simply add the total units 612+612+816 for 2,040 domestic water units which would bring me to 325 gpm for all three buildings. Add to this the 60 gpm for sprinklers and I would have a total of 385 gpm sprinkler and domestic from the point of the 4" connection to the 8" loop to the city water main.
I will probably go with the 385 gpm just to play safe and avoid any possible argument.
So how would you handle this?
Travis? I know you have run into this a lot.
Construction just started and my drawings are about 50% completed.