Neel.mech
Mechanical
- Mar 22, 2014
- 26
hello all,
I working on a weird project, we have a dedicated fire pump ( 750 gpm @ 60 psi) for a foam system which is tapped off from sprinkler tree. Distance b/w fire pump & sprinkler room is about 300 meters. we are getting only 170 gpm and about 5 psi at suction and fire pump didn't kick in when tested & manufacturer rep shut it down as there is no required flow. . is this design against NFPA reliable water supply?.
incoming line from sprinkler room is 6 " and available pressure on the hydrant outside is 44 psi when tested. wondering if anyone came across something similar ? any possible solutions ?
I working on a weird project, we have a dedicated fire pump ( 750 gpm @ 60 psi) for a foam system which is tapped off from sprinkler tree. Distance b/w fire pump & sprinkler room is about 300 meters. we are getting only 170 gpm and about 5 psi at suction and fire pump didn't kick in when tested & manufacturer rep shut it down as there is no required flow. . is this design against NFPA reliable water supply?.