reluminate
Electrical
- Sep 19, 2011
- 4
I'm working on determining the electrical classification in a building that has a storage room where they store Class 1B flammable liquids. As I read Table 7.3.3, that entire room would be classified as NEC Class 1, div 2, zone 2.
There are other indoor rooms in the building adjacent to this storage room that have doors opening into it. These rooms are used for warehousing non-flammable liquids, offices, labs and electrical room.
If I'm interpreting Table 7.3.3 correctly, if an ordinary classified room opens into a room that is entirely classified, then that room is also entirely classified. Is this a correct interpretation? If so, what about rooms that open into rooms that open into rooms that are classified?