NFPA 30 Tank Separation Calculations

Status
Not open for further replies.

jmk0407

Mechanical
Aug 22, 2013
13
How does one calculate tank separation distances for groups of tanks larger than 2 x 2 in accordance with NFPA? Say if I have a grid of 3 x 3 storage tanks, all floating roof, all flammable for the sake of this question. Is it one uniform tank distance calculated by summing every possible adjacent tank diameter combinations and dividing by 6? It seems like the number will be excessively large if I follow the methodology as described for 2 tanks by 2 tanks as explained in the NFPA 30 handbook. Thank you for your assistance.
 
Replies continue below

Recommended for you

Calculate each pair of adjacent tanks separately. The resulting grid may not be regular if the tank sizes vary.
 
stookeyfpe - I can sometimes answer the easy questions, as I personally interpret the codes. You guys do the heavy lifting, thanks!
 
Thanks for your help! I wasn't sure what would be a more appropriate forum but figured that there is enough overlap.
 