hssmiguel
Mechanical
- Sep 26, 2013
- 5
Hi everybody,
I'd like to ask you about your understanding of NFPA 850 point 6.2.2, related to the water supply. Do you interpret from this point that more than one tank (source?) for fire protection purposes is needed (recommended) in a power plant? I usually consider only one tank as source for fire fighting system demands.
For instance, when I estimate a flow for transformers deluge system, I add to it the hose stream demand of 500 gpm (1890 L/min) and I get a capacity multypling it by 2 hours, which I consider as the total water volume to be storaged. Would it be right, or should I consider two sources with this volume each?
Thank you in advance!
I'd like to ask you about your understanding of NFPA 850 point 6.2.2, related to the water supply. Do you interpret from this point that more than one tank (source?) for fire protection purposes is needed (recommended) in a power plant? I usually consider only one tank as source for fire fighting system demands.
For instance, when I estimate a flow for transformers deluge system, I add to it the hose stream demand of 500 gpm (1890 L/min) and I get a capacity multypling it by 2 hours, which I consider as the total water volume to be storaged. Would it be right, or should I consider two sources with this volume each?