Hello
Currently, I am working on finding a solution for smoke extraction in an atrium building. The building has 5 floors with 10.000 sqft each. According to the NFPA 92, this is a type of spill plume, since the fire would start on one of the floors and spill to the open space in the middle. The problem is that the hole that represents the atrium is relatively small compared to the floor area (about 1000 sqft) and has escalators in it. So, there is no much room left for the smoke to go through, and once in the atrium, it gets easy to the upper floors where it poses danger to the people. NFPA 92 describes the atrium buildings where the atrium has a huge area and smoke is able to rise up more or less freely. Here, I have a hole in the ceiling where a lot of smoke comes through, from all four sides.
There is a smoke extraction point at the top of the atrium with a capacity of volumetric flow rate of 45 m3/s. The fire calculated spreads according to t2 curve (fast) and reaches around 1.5 MW before the sprinkler activates (each floor is equipped with sprinklers).
Using NFPA 92 calculation methods I get very high volumetric flow rates required to make proper smoke extraction. Is there any other way to address this specific case of the atrium?
Would be better to use a mechanical supply inlet instead of just natural inlet openings? Although the velocities of inlet air would be fine, I have concerns once the sprinkler activates. It will effectively lower the smoke temperature and take away some of its buoyancy.
Currently, I am working on finding a solution for smoke extraction in an atrium building. The building has 5 floors with 10.000 sqft each. According to the NFPA 92, this is a type of spill plume, since the fire would start on one of the floors and spill to the open space in the middle. The problem is that the hole that represents the atrium is relatively small compared to the floor area (about 1000 sqft) and has escalators in it. So, there is no much room left for the smoke to go through, and once in the atrium, it gets easy to the upper floors where it poses danger to the people. NFPA 92 describes the atrium buildings where the atrium has a huge area and smoke is able to rise up more or less freely. Here, I have a hole in the ceiling where a lot of smoke comes through, from all four sides.
There is a smoke extraction point at the top of the atrium with a capacity of volumetric flow rate of 45 m3/s. The fire calculated spreads according to t2 curve (fast) and reaches around 1.5 MW before the sprinkler activates (each floor is equipped with sprinklers).
Using NFPA 92 calculation methods I get very high volumetric flow rates required to make proper smoke extraction. Is there any other way to address this specific case of the atrium?
Would be better to use a mechanical supply inlet instead of just natural inlet openings? Although the velocities of inlet air would be fine, I have concerns once the sprinkler activates. It will effectively lower the smoke temperature and take away some of its buoyancy.