NFPA USE OF QUICK RESPONSE

Status
Not open for further replies.

engggu

Mechanical
Apr 4, 2021
39
HI EXPERTS,
May I know if the use quick response sprinklers are required for the residential areas like condominiums?

Or standard sprinklers can also be used on the dwelling units.

Thank you
 
Replies continue below

Recommended for you

residential areas need fast response residential sprinklers. in the past standard spray sprinklers were allowed in order to get existing buildings retrofit with fire sprinklers.
 
It depends on the standard the project is using to design. If 13R, must use residential in the dwelling unit. You can have up to 4 QR sprinklers in the dwelling unit. If NFPA 13, you can do QR sprinklers in lieu of residential sprinklers. You will likely end up with larger pipe sizing.

Travis Mack, SET, CWBSP, RME-G, CFPS
MFP Design, a Ferguson Enterprise
 