I have to protect a feeder with SEL-751, I was asked to do 50N and 51N,
On the source side, the feeder is connected to the NGR-grounded-Wye side of a Delta-Wye transformer; on the load side it is connected to the Delta side of a Delta-Wye grounded transformer, so there is no steady state 3I0 flowing under normal conditions due to any load unbalance; there is a 50/5 CT in the transformer neutral connected to the SEL-751.
For 50N, I have simply ran a L-G fault and set the relay slightly under the obtained result, but how may I set up 51N, if there is no say "allowed unbalance" at all ? What would be the pick-up setting ? Which curve to use ?
The NGR is rated 25A for 10 seconds,
Thanks a lot, any help will be very appreciated,
Best regards,
Mongao
I have to protect a feeder with SEL-751, I was asked to do 50N and 51N,
On the source side, the feeder is connected to the NGR-grounded-Wye side of a Delta-Wye transformer; on the load side it is connected to the Delta side of a Delta-Wye grounded transformer, so there is no steady state 3I0 flowing under normal conditions due to any load unbalance; there is a 50/5 CT in the transformer neutral connected to the SEL-751.