I recently replaced a FCU for a customer with a like-for-like unit. To my surprise, when we opened the valves, we experienced no water flow through the unit. The customer then informed me the system hasn't worked for 8 years or so, and I should just hot tap a different supply line (I thought that was sort of strange). After tapping the new line and running new pipe, the system still didn't work.
I have removed the chill water control valve from the system and am recording 120 PSI on both sides of the coil. Of course, without a differential pressure, water won't flow, so I have concluded the customer has a water flow issue (aka water pressure issue). The customer, however quickly stated he has no issue and I just need to upsize the pipe.
The size pipe I am currently using requires a pressure drop of 6.9 PSI; upsizing will require only 5.3 PSI. Should that little of a difference (1.6 PSI) really matter?
I have removed the chill water control valve from the system and am recording 120 PSI on both sides of the coil. Of course, without a differential pressure, water won't flow, so I have concluded the customer has a water flow issue (aka water pressure issue). The customer, however quickly stated he has no issue and I just need to upsize the pipe.
The size pipe I am currently using requires a pressure drop of 6.9 PSI; upsizing will require only 5.3 PSI. Should that little of a difference (1.6 PSI) really matter?