No voltage from generator when neutral and ground connected together

Status
Not open for further replies.

wiks

Electrical
Jan 31, 2003
4
0
0
LV
Hi everyone!

So I have problem with portable diesel generator.

Generator: 3 phase
AVR has one feeding winding , one sensing winding and outcome DC goes to rotor winding.

All are right when Neutral and Grounding are separate. When I grounded the neutral voltage disapears.

So what could be wrong?
 
Replies continue below

Recommended for you

You may have a ground fault on one of the windings. Check for a voltage between neutral and ground with the neutral floating. Megger the windings and do a resistance check with a multi meter from any winding to ground with the neutral floating.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Check the AVR connections as well. Its possible that there's an internal jumper between ground and some other input/output that is incompatible with a grounded neutral.
 