Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Nominal vs Float DC arcflach calculations

Status
Not open for further replies.

AppleJaxJap

Electrical
Jul 1, 2016
17
0
0
US
can not find guidance in 70E or IEEE.


This issue makes VERY little difference in the calculation BUT I still want the reference

UPS
40 bats @ 12V = 480Vdc But
Float voltage is 2.25V Per Cell so the actual voltage on the bus when maintenance is being done is 2.25 x 6 x 40 = 540Vdc
I use the 540Vdc in the AF calculation as it provides a more conservative result (CYA)

Where this really makes a difference is in 96Vdc inverters.
<100Vdc does not need a calculation done but if you use the float voltage you are at 108Vdc and it does.

looking for some reference IEEE or other white papers that might provide guidance on this calculation voltage should be used.

This is your life and its ending one moment at a time.
 
Replies continue below

Recommended for you

IEEE 1375-1998 "Guide for the Protection of Stationary Battery Systems," has some relevant information. Section 6.6.2 suggests that the higher float charging voltage only increases the short circuit current by about 1%. The reason being that although the voltage is higher, the chemical capacity of the battery to supply fault current is mostly unchanged. So for your arc flash calculations you might be justified in using the nominal DC voltage, but with the fault current increased by 1%.

There is also the fault current contribution of the battery charger itself, though for modern power electronic devices I wouldn't expect that to be much more that 1.5x nominal current.
 
Status
Not open for further replies.
Back
Top