Non-contact infrared temperature control.... 1
davek0974
6
Hi all, first post:)
I have a question reagrding interface methods.
We have a printing press in the shop, it has an infrared dryer built in, it's basically 8kw of halogen lamps controlled by a thyristor stack power controller and temperature is user adjusted by a potentiometer. The printed sheets pass under this lamp array for a split second on their way out of the press to the delivery stack. For maximum effect, the printed paper stack should be maintained at a temperature of 30-35c, any less and it has little or no effect, much more and there is a risk of the stack catching fire due to the ink solvents on the sheets etc.
This temperature is under user control but measurement is also done manually, I use a laser/infrared thermometer at regular intervals and set the knob where I think it should be. This is not perfect as the stack temperature is machine speed dependant and paper type dependant - thicker paper warms up slower etc.
I am working on a way of making it closed-loop, i.e. building in some sort of IR thermostat to give a variable output based on a set-point?
I have sourced a suitable non-contact pyrocouple and a process controller but here we hit a snag, i need to integrate without altering the existing machine in any severe way.
I know the potentiometer is used in a two-wire config, and not as i had hoped as a three-wire potential divider whereas i could simply output a suitable voltage to control the power.
So i am looking for ways to control without alteration. Is there such a thing as an electronic variable resistance that could be wired in series with the existing pot?? It could be controlled by a 0-10v or 4-20mA signal?
Anyone got any interface ideas that might work here? I had even thought of a pwm controller and a simple radio-control servo which could connect physically to the existing knob. It only uses a small portion of the 270deg span of the pot, maybe 90deg total.
Any thoughts would be very much appreciated.
Yours
Dave Kearley
I think your question is far to complicated to be answered here. You are trying to automate the simplest part of your control. Start-up and shutdown is where you will be starting fires.
Thanks,
I thought it might be a tough one, maybe I'd be better on an electronics forum?
Startup and shutdown is already handled by the base machine, all I need to do is find a way of altering the position of a control knob based on a sensed temperature, scaling, limits and so on are all handled by the process controller.
Dave
You could put a transistor in series with the variable resistor and control the transistor with your controller.
Thanks Brian,
I can see that being possible but would need some resistor padding etc to get the 0-10v signal to control the transistor properly, only trouble with that is - I am useless with discrete components, I'm ok with PLC's, Process controllers, pneumatics and maybe even valves :) but never done any design with transistors.
I can likely find the voltage i am dealing with easily and being a standard film pot, the power wont be >1W so its a small load.
Its just the scaling 0-10v = off to on gradually thing i cant deal with.
Just found that a J-FET will do this but again, beyond my knowledge.
Any ideas??
Dave
Ok, finally had a chat with the manufacturer. He sent me a diagram of an add-on board that was used for 4-20mA control loop operation of the unit, i have sketched it out and attached it.
VR1 is the existing set point control, this must remain in circuit.
I have no values for the other components.
It seems this is exactly what is needed so i just need to fill in the blanks i guess.
 http://files.engineering.com/getfile.aspx?folder=8bfa9200-810e-42ad-9eb0-56628067a652&file=Ma1.bmp
I think you're mixing up the "setpoint" to the controller (your variable pot) with the "feedback" that the controller uses to monitor temperature.
Correct me if I'm wrong, but I think you want to use the pot to set a temperature and use the ouput of the pyro in the control loop, so, for instance, if you command the pot for a temperature of 200 degrees and the pyro says you're only at 190 degrees then the heaters would turn on. Is this correct?
Ok, the only reason that the existing pot is left is because the circuit required it. I would prefer to use the process controller to do all the work. I have since noticed that anything that varies the resistance will likely do ok.
The vactrol mentioned or even simpler an LDR and lamp driven from the 0-10v output of the controller should work, as far as I understand it, a lower resistance = more power.
I could wire an LDR in series with the existing pot which would then give me an adjustable max limit, the answer is now within the realms of a few experiments I think.
Thanks for all the advice
Dave
