Hi Everyone – I’ve summarized your comments and put my replies below. I hope to be able to video the voltmeter with the kettle running and fridge starting up. The fridge problem is only when the genset is on.
waross (Electrical)24 Apr 24 15:24 - Well noted. I will video the voltmeter tomorrow.
Does the generator have auto-start?
The fridge may not be drawing enough current to activate auto-start. There are a 5 - 20W lights, 2 - 45W laptop chargers, 4 - 50W fans, another but smaller fridge (94W consumption)
Try it with the switch on the generator in the RUN position rather than the AUTO position.
Don't worry about filament lamps.
Look at the voltmeter instead.
davidbeach (Electrical)24 Apr 24 21:07
Does the fridge have internal overvoltage protection that keeps it from running until the kettle pulls the voltage down? Can you advise me on how to check if the fridge has overvoltage protection?
jghrist (Electrical)25 Apr 24 02:29
Sounds like you have an open line to one side of the line-line 240V connection to the fridge. The fridge then gets voltage when there is a connection from neutral to the line through the kettle. This sounds quite plausible. However, on some occasions the fridge will start up without the kettle being started. In these cases, it does not stay on more than a minute. Would this negate your theory? BTW we are in Zambia.
I had a similar problem during an outage where one leg of my 120/240V service was open. I could get lights on the open leg only when my 240V water heater was on. I would take a shower in the dark until the water heater came on, then my bathroom lights would work at partial voltage.
If you are in Europe or the UK where the service is 230/400V, maybe your kettle provides a connection between the neutral to the other phase. Chances are this is the case because 230V fridges are not normal in North America.
davidbeach (Electrical)25 Apr 24 03:34 Noted.
Likely single phase-neutral 230V. Open neutral was my first thought as well, but that’s a North America thing. The generator is single phase but the utility provides 3 phase.
LittleInch (Petroleum)25 Apr 24 07:31
I hope you have a procedure where you disconnect the incomer before turning the generator switch on. The selector on the white box selects the power source. To be frank that connection is very dangerous and with only one connection for a 6KVA generator is dangerous. I agree its very dangerous. I am a tenant and not the owner.
But the issue would seem to be your fridge is sensitive to voltage or frequency and your generator needs a load to stabilise it.
Do you have a heater you can connect? No heater available. Current outdoor temperature around 85 – 90F. This genset won’t power on the 24,000 BTU aircon.
But first start looking at the voltages supplied before and after the kettle is turned on and off. I missed the opportunity for this today but hopefully tomorrow.
That generator looks rather old and I suspect its control of voltage is now rather poor. The voltmeter needle did not seem to vary from about 230 V today. But from my calcs the genset is certainly undersized for the demands at the two houses, and it has never started the aircon.
Remember - More details = better answers. Well noted.
Also: If you get a response it's polite to respond to it. Well noted.