Null area load assignments

Status
Not open for further replies.

rscassar

Structural
Jul 29, 2010
631
Has Etabs v19 got a method for using null areas for load assignments. I remember using this tool in v18.0.1 but this function seems to have discontinued.
 
Replies continue below

Recommended for you

@rscassar Null area in ETABS does not Transfer loads right?
 
it use to transfer load assignments but doesn't anymore

Link
 
You can still use Null area to assign superimposed loads on top of structural slab or deck. See proof below.
A2 is null area 6x6 loaded 100psf. F2 is one-way load distribution deck.
image_s6hee4.png


Here is the caveat: This works wonder if you model everything in coordinate system with System Origin Rotation = 0. If it is rotated, ETABS will f.ck it up. Check it out yourself.
image_cyhhyq.png
 