numbering convension for Motor starter controls and contacts
mshahwan
7
CA
is there a standard for the numbering convention for motor starters? like NO/NC contacts, 11-14,12-13, or coil ,A1-A2?
thanks in advance
Probably EN 50013 if you are in Europe, which I think you are looking at the number codes.
image.php
I found some explanation in NEMA ICS 2.4 which explains the difference between NEMA and IEC motor control devices.
NEMA has no numbering convension for control terminals
IEC
NC Contact
11
12
first digit designate sequence of control terminal second designals NC contact
23
24
first digit disignates sequence of control terminal second designates NC contact
A1
A2
coil terminal markings
Anybody know the exact standard for IEC that specifies this?