DHEngineer
Mechanical
- Aug 25, 2010
- 4
Hello All,
I am new to the forum and have the following question regarding Combined Automatic Wet Sprinkler / Manual Wet Standpipe systems in NYC under the latest code. For some reason the code does not address this.:
I am working on a low rise I1 occupancy building that requires an automatic sprinkler system as well as a standpipe system due to the area floor limitations. According to the NYC code, I can install a class 1 standpipe system in leu of a Class 3 system provided the usual requirements are met (lobby cabinet ect..)
After then reading NFPA 14 as modified by appendix Q, it states that in low rise buildings, Class 1 standpipes may be automatic wet or manual wet. So Far so good. At this point I have decided to go with the combined automatic wet sprinkler / manual wet standpipe system.
Based on the above, I assume that I will only have to provide a pump to satisfy the load of the sprinkler system and size the system pipes to accomidate the sprinkler system fed from the building pump and standpipe load that will be fed from the FD siamese connection. Again, so far so good.
Here is where it gets tricky. Since my building pump will only be providing the supply for the building sprinkler and only maintaining the water in the manual standpipe system, am I then allowed to use a sprinkler booster pump with one source of water? Or am I required to provide a fire pump with two sources of water?
I can not find this in the code anywhere and have yet to find a difinitive answer from a NYC code official.
Please let me know if anyone has had any experience with this in NYC or if any of my Logic seems off on any of the above.
Thanks,
DHEngineer
I am new to the forum and have the following question regarding Combined Automatic Wet Sprinkler / Manual Wet Standpipe systems in NYC under the latest code. For some reason the code does not address this.:
I am working on a low rise I1 occupancy building that requires an automatic sprinkler system as well as a standpipe system due to the area floor limitations. According to the NYC code, I can install a class 1 standpipe system in leu of a Class 3 system provided the usual requirements are met (lobby cabinet ect..)
After then reading NFPA 14 as modified by appendix Q, it states that in low rise buildings, Class 1 standpipes may be automatic wet or manual wet. So Far so good. At this point I have decided to go with the combined automatic wet sprinkler / manual wet standpipe system.
Based on the above, I assume that I will only have to provide a pump to satisfy the load of the sprinkler system and size the system pipes to accomidate the sprinkler system fed from the building pump and standpipe load that will be fed from the FD siamese connection. Again, so far so good.
Here is where it gets tricky. Since my building pump will only be providing the supply for the building sprinkler and only maintaining the water in the manual standpipe system, am I then allowed to use a sprinkler booster pump with one source of water? Or am I required to provide a fire pump with two sources of water?
I can not find this in the code anywhere and have yet to find a difinitive answer from a NYC code official.
Please let me know if anyone has had any experience with this in NYC or if any of my Logic seems off on any of the above.
Thanks,
DHEngineer