I have been in the electrical industry for 50 years. I am now engaged in performing commission inspections and related tests of new building electrical systems.
I am finding current on all equipment ground conductors to power transformers in the facilities.
This is due to the X-O of the secondary being effectively(earthed) at a point other than at the service ground electrode location.
I have been insisting the X-O ground conductor be routed back to the main service ground point.
The latest edition of the Soares Grounding Book,illustrates the many grounding methods that create two or more ground paths and points.
I would like some of the intellects on this forum to give me their opinion of Chapter 12, 8th Edition, of the Soares Book. This publication is now sponsored by the IAEI.
I feel this book is incorrect and creating many inferior designs of ground systems, with objectionable current flow from interior and exterior systems.
On another issue;
Generator separately derived system in same publication.
I can not see where the utility neutral is being disconnected by the transfer switch, when it is shunted by the ground conductor.
Need all the expert comments I can get. Thanks; Bennie
I am finding current on all equipment ground conductors to power transformers in the facilities.
This is due to the X-O of the secondary being effectively(earthed) at a point other than at the service ground electrode location.
I have been insisting the X-O ground conductor be routed back to the main service ground point.
The latest edition of the Soares Grounding Book,illustrates the many grounding methods that create two or more ground paths and points.
I would like some of the intellects on this forum to give me their opinion of Chapter 12, 8th Edition, of the Soares Book. This publication is now sponsored by the IAEI.
I feel this book is incorrect and creating many inferior designs of ground systems, with objectionable current flow from interior and exterior systems.
On another issue;
Generator separately derived system in same publication.
I can not see where the utility neutral is being disconnected by the transfer switch, when it is shunted by the ground conductor.
Need all the expert comments I can get. Thanks; Bennie