Bisbee_Structural
Structural
I find Occupied Roof Live loads to be very inconsistent in the ASCE/IBC and would appreciate your input!
What live loads do you use for a residential occupied roof (single-family)?
ASCE 7-16 Table 4.3-1 allows for a live load at the roof same as the occupancy served, which for a house would be a 40 psf live load. This was first introduced in ASCE 7-10.
IBC 2018 Table 1607.1 has no similar allowance for a residential occupancy. The only live loads given are for Roof Gardens (100 psf), Assembly Areas (100 psf), and "all other similar areas" which refers to footnote l: "Areas of occupiable roofs, other than roof gardens and assembly areas, shall be designed for appropriate loads as approved by the building official". This was first introduced in IBC 2012.
IBC 2009 Table 1607.1 gives live loads for Roofs used for promenade purposes (60 psf), Roofs used for roof gardens or assembly purposes (100 psf), and "Roofs used for other special purposes" which refers to footnote l: "Roofs used for other special purposes shall be designed for appropriate loads as approved by the building official"
I can't find specific recommendations for my project jurisdiction (NY State).
My thoughts:
1) In my judgement 40 psf is too little for a roof deck, and 100 psf is too conservative.
2) In the past I have used a live loads of 1.5 times the live load of the area served, based off the of the live load requirements for balconies and decks. 60 psf seems more appropriate to me, assuming people will crowd onto a roof similar to a balcony/deck. In the absence of more specific requirements from the authority having jurisdiction this seems like a reasonable and defensible position under footnote l of the 2018 IBC.
3) I am uncertain how this fits with the category 'roof garden' defined in the commentary in the 2018 IBC: "Roof gardens are landscaped areas where assembly use is not anticipated, such as a promenade deck located on the main roof of an apartment building". This seems to push towards a 100 psf live load even in roofs where assembly use is not anticipated.
4) My project features an occupied roof with a paved pedestal roof deck system and an extensive green roof system not explicitly designed for occupants but also not physically separated from the roof deck by railings/guards etc. Based on the above, I would assume 60 psf for the paved deck and 100 psf for the green roof. But this seems illogical- why would the green roof have a higher live load than the adjacent paved deck?
I would greatly appreciate any and all input!
What live loads do you use for a residential occupied roof (single-family)?
ASCE 7-16 Table 4.3-1 allows for a live load at the roof same as the occupancy served, which for a house would be a 40 psf live load. This was first introduced in ASCE 7-10.
IBC 2018 Table 1607.1 has no similar allowance for a residential occupancy. The only live loads given are for Roof Gardens (100 psf), Assembly Areas (100 psf), and "all other similar areas" which refers to footnote l: "Areas of occupiable roofs, other than roof gardens and assembly areas, shall be designed for appropriate loads as approved by the building official". This was first introduced in IBC 2012.
IBC 2009 Table 1607.1 gives live loads for Roofs used for promenade purposes (60 psf), Roofs used for roof gardens or assembly purposes (100 psf), and "Roofs used for other special purposes" which refers to footnote l: "Roofs used for other special purposes shall be designed for appropriate loads as approved by the building official"
I can't find specific recommendations for my project jurisdiction (NY State).
My thoughts:
1) In my judgement 40 psf is too little for a roof deck, and 100 psf is too conservative.
2) In the past I have used a live loads of 1.5 times the live load of the area served, based off the of the live load requirements for balconies and decks. 60 psf seems more appropriate to me, assuming people will crowd onto a roof similar to a balcony/deck. In the absence of more specific requirements from the authority having jurisdiction this seems like a reasonable and defensible position under footnote l of the 2018 IBC.
3) I am uncertain how this fits with the category 'roof garden' defined in the commentary in the 2018 IBC: "Roof gardens are landscaped areas where assembly use is not anticipated, such as a promenade deck located on the main roof of an apartment building". This seems to push towards a 100 psf live load even in roofs where assembly use is not anticipated.
4) My project features an occupied roof with a paved pedestal roof deck system and an extensive green roof system not explicitly designed for occupants but also not physically separated from the roof deck by railings/guards etc. Based on the above, I would assume 60 psf for the paved deck and 100 psf for the green roof. But this seems illogical- why would the green roof have a higher live load than the adjacent paved deck?
I would greatly appreciate any and all input!