I just received the results of the oil analysis we made on a 2.5 MVA transformer. I'm a little puzzled by the results and I would like to have your opinion.
We have the results from the last 4 years.
The DGA show stable gasses (low concentrations) and no problem have been observed on that transformer.
But look at the oil properties:
(values for 2003 2004 2005 2006)
Dielectric breakdown (kV) :
51.5 46.9 35.2 18.6
Neutralization number (mg KOH/g):
0.028 0.036 0.044 0.052
Color:
1.5 1.5 1.5 1.5
Interfacial Tension (Dynes/cm):
26.2 27.9 25.3 26.9
Water (ppm):
7 3 8 14
Oxidation Inhibitor (% DBPC):
(2005 2006)
0.18 0.16
There is more than enough oxidation inhibitor and we observe what looks like oxidation results (Neut. N. increases, DB lowering, low IFT), but the DB is falling really fast! I think a treatment with fullers earth is necessary, but can't explain why this happened with enough oxidation inhibitor!
Anything else could explain those results (sample contamination, analysis errors?)
We have the results from the last 4 years.
The DGA show stable gasses (low concentrations) and no problem have been observed on that transformer.
But look at the oil properties:
(values for 2003 2004 2005 2006)
Dielectric breakdown (kV) :
51.5 46.9 35.2 18.6
Neutralization number (mg KOH/g):
0.028 0.036 0.044 0.052
Color:
1.5 1.5 1.5 1.5
Interfacial Tension (Dynes/cm):
26.2 27.9 25.3 26.9
Water (ppm):
7 3 8 14
Oxidation Inhibitor (% DBPC):
(2005 2006)
0.18 0.16
There is more than enough oxidation inhibitor and we observe what looks like oxidation results (Neut. N. increases, DB lowering, low IFT), but the DB is falling really fast! I think a treatment with fullers earth is necessary, but can't explain why this happened with enough oxidation inhibitor!
Anything else could explain those results (sample contamination, analysis errors?)