I am having a problem with a Honeywell oil furnace flame sensor control. It is, IMHO, a design issue as it has been a problem for years since it was new. Maybe someone can tell me how to solve it. I am a retired EE so I can't just replace it (u know how that goes) and everything else has the same ckt so they probably will all act the same. The attachment shows the ckt. Everything works fine as long as there are no power interruptions. Unfortunately, this house is in the mts and when there is a storm of any kind the power does strange things. The other issue is, I don't live there. It is a vacation home and things freeze when it trips out.
I thought that it might be because the burner was shut down and restarted too fast so I put a TD relay in the thermostat ckt. One blew out (permanently open) and the ckt tripped at the same time.
I am now thinking that a rapid off/on of the power is generating an inductive spike on the secondary of the transformer which is getting to the triac and turning it on, and may have fried the TD relay.
ckt operation: When the thermo goes on, 24V is applied across R1 and the CAD cell (high resistance) and the triac is turned on. This pulls in K1, which starts the burner and holds the relay on. When the CAD cell sees a flame, its resistance drops and turns off the triac, and everything runs fine. If it does not see a flame in about 20 sec. the heater trips the safety sw. and everything shuts down.
The 1st question is, if there is a power transition is it reasonable to assume an inductive spike will be generated on the secondary?
The 2nd question is, if the TD relay trips in 10ms after power failure, the safety sw must trip out before K1 drops out. This I cannot explain - IE, what sequence of events will do this?
The 3rd question, how to I stifle it?
One thought is to place the TD relay in the primary of the transformer. I have not done this because it involves surgery on the control unit. But I am about to as soon as someone can explain #2. Maybe sooner.
The TD relay will not come back on for 5 min. after power is restored.
Thanks in advance for ANY ideas.
I thought that it might be because the burner was shut down and restarted too fast so I put a TD relay in the thermostat ckt. One blew out (permanently open) and the ckt tripped at the same time.
I am now thinking that a rapid off/on of the power is generating an inductive spike on the secondary of the transformer which is getting to the triac and turning it on, and may have fried the TD relay.
ckt operation: When the thermo goes on, 24V is applied across R1 and the CAD cell (high resistance) and the triac is turned on. This pulls in K1, which starts the burner and holds the relay on. When the CAD cell sees a flame, its resistance drops and turns off the triac, and everything runs fine. If it does not see a flame in about 20 sec. the heater trips the safety sw. and everything shuts down.
The 1st question is, if there is a power transition is it reasonable to assume an inductive spike will be generated on the secondary?
The 2nd question is, if the TD relay trips in 10ms after power failure, the safety sw must trip out before K1 drops out. This I cannot explain - IE, what sequence of events will do this?
The 3rd question, how to I stifle it?
One thought is to place the TD relay in the primary of the transformer. I have not done this because it involves surgery on the control unit. But I am about to as soon as someone can explain #2. Maybe sooner.
The TD relay will not come back on for 5 min. after power is restored.