- Apr 6, 2016
- 23
This is regarding Oil filled Transformer derating for ambient higher than 30degC as per IEEE C57.91.
The specified values are 1.5% for each deg C rise above for Self Cooled and 1% for each deg C rise for Forced air Cooled.
If I have a 60/80 MVA ONAN/ONAF Xmer, and the average max is 45degC, does it mean that ONAN rating of 60MVA needs to be derated by (45-30)x1.5=22.5% and the ONAF rating by (45-30)x1=15% ????
Or in case of ONAN/ONAF rated Xmers, both the OA and FA ratings are to be derated by 1% per degC rise?? i.e 15% derating for both 60MVA and 80MVA?
Need clarification on the above. Thanks.