hello
An electrical oil transformer of 35KVA step up 11KV/20KV has tripped by
-bucholoz relay -differentiation protection -50N
An Insulation test for windings gave : 170 Kohm in sec / 4Mohm in primary
Oil Dielectric test tripped in 13KV..
after oil regeneration done :
Oil Dielectric test now tripped in 40KV but the windings Insulation still 170Kohm for sec and 4Mohm for Pri.
my questions are :
1)Are the Dielectric oil test is enough to tell the oil is good or I need to make other test?
2) How can I confirm that the windings has low insulation not because of the oil?