maxPE
Nuclear
- Feb 1, 2003
- 21
I have some nuisance tripping of distribution line fuse links feeding a pad mount transformer. I suspect the fuse is not appropriate for the transformer. The transformer is rated at 45 kW, primary voltage is 4800, secondary is 480. The load is a 40hp motor with a soft start/stop so the inrush is zip. The blown link was a 7 amp K fuse. If I assume the transformer P.F is .8, the transformer would be rated at 56kVA? Is that correct? IF that is true, the line fuse link should be about 10 amp and I am thinking a slower fuse link would be better like a type X or?
Thanks for any advice.
Thanks for any advice.