OLTC+AVR Problems

Status
Not open for further replies.

kobenaw

Mining
Oct 16, 2011
2
We have an OLTC with Alstom MVGC as the AVR. Recently, we have been going down a lot on out of step. This is because we have a parrallel connected transformers with master-follower configuration. The problem only occurs between taps 4 and 5. The master moves to 5 but the follower stays at 4. What are the things to look out for?
 
Replies continue below

Recommended for you

Has the transformer previously gone past step 4 or is this a new installation? Is there a tap range limiter?
 
The transformer has gone past step 4 until recently. There is tap range limiter for tap 16, the last tap.
 
If the tap changer master-follower unit is tested and commissioned properly, falling out of step during the operation is quire rare.
Would it be a wiring problem?
 
Does the follower relay on the tap position indicator? If so then ensure that the TPI is operating correctly - many use a series of low resistance steps and have low excitation voltages which can easily be affected by oxidation and dirt on the contacts.
 
Is tap zero the neutral tap? If the transformer is +7.5%/-2.5%, tap 5 might indicated a problem with the neutral.

Which method of master/follower are you using? We had one location where the follower command was driven by the sealed in raise contact on the master. Once in a while, the follower would finish tapping a fraction of a second faster than the master, and would start a second tap change just before the master finished.
 