mnovicki
Structural
- Feb 4, 2008
- 13
My question is in regard to the design of a steel OMF connection. For architectural reasons, we have provided beams and columns that are much larger than required. The plastic hinge will form in the column. My understanding of AISC 341 is that I must design using the force delivered to the connection of 1.1*Ry*Mpcol. This results in forces exceeding the anticipated seismic forces on a scale of at least ten times, probably way more. In my case I have a wide flange framing into an HSS. Do I really need to use these elevated forces for AISC 360 Chapter K checks on the HSS, considering my members sizes are oversized? Then there is a blurb in 11.2a(4)of 341 that says a lesser value of Va is permitted if justified by analysis. "The required shear strength need not exceed the shear resulting from the application of appropriate load combinations in the applicable building code using amplified seismic load". Is this true for the tension and compression forces from the flange as well?