John_187
Mechanical
- Apr 21, 2018
- 68
This question is about waste stacks and and relief vent connections at the base of the stack.
The situation is a toilet only waste stack and vent stack that is 5 stories tall. There is a dedicated 2" vent stack and 4" waste stack for these toilets. First section 907 of the 2015 IPC mentions relief vent connections for horizontal offsets for waste stacks 5 stories or more.
However, 711.2.1 and 711.3 over ride the requirement for a vent connection at the stack base though. As long as the waste stack piping is sized at 1 size greater than requirements for a building drain (Which it is at 4"), no relief vent at the base of the stack is required. The concept is that over sized stacks minimizes any positive pressure developed by slugs going down the stack.
Another aspect of this, is these toilet stacks terminate in a parking garage space above ground. They turn horizontal and are connected to nearby bathroom lav and shower waste stack vents. Some of these lav and shower stacks might be 3-4 feet away from the toilet stacks. All these collect and route down columns in the garage then go below grade. This is the only thing I'm not sure about with this - I don't know if these lav stacks or shower stacks qualify as "horizontal branch connections" downstream of the lowest toilet stack offset. It does't define this aspect of it. But still, the toilet waste stack is 4", so the thought is pressure developed would be minimized because of that over sized waste stack.
See attached document with code sections and diagrams. Do you believe that no relief vent connection is required for this situation?
Thanks for any input. Venting is most obscure, hard to interpret part of plumbing
The situation is a toilet only waste stack and vent stack that is 5 stories tall. There is a dedicated 2" vent stack and 4" waste stack for these toilets. First section 907 of the 2015 IPC mentions relief vent connections for horizontal offsets for waste stacks 5 stories or more.
However, 711.2.1 and 711.3 over ride the requirement for a vent connection at the stack base though. As long as the waste stack piping is sized at 1 size greater than requirements for a building drain (Which it is at 4"), no relief vent at the base of the stack is required. The concept is that over sized stacks minimizes any positive pressure developed by slugs going down the stack.
Another aspect of this, is these toilet stacks terminate in a parking garage space above ground. They turn horizontal and are connected to nearby bathroom lav and shower waste stack vents. Some of these lav and shower stacks might be 3-4 feet away from the toilet stacks. All these collect and route down columns in the garage then go below grade. This is the only thing I'm not sure about with this - I don't know if these lav stacks or shower stacks qualify as "horizontal branch connections" downstream of the lowest toilet stack offset. It does't define this aspect of it. But still, the toilet waste stack is 4", so the thought is pressure developed would be minimized because of that over sized waste stack.
See attached document with code sections and diagrams. Do you believe that no relief vent connection is required for this situation?
Thanks for any input. Venting is most obscure, hard to interpret part of plumbing