I am used to seeing a circuit breaker, or fuses, used with a contactor and overload relay in motor control circuits.
However, we've taken delivery of a feeder conveyor which uses a large circuit breaker to supply the two motors on the conveyor, with a contactor and overload relay for each motor.
The exact details of the circuitry are as follows:
Main incomer circuit breaker rating on the conveyor - 630A
Contactor rating 185A - 2 off connected in parallel for each motor.
Electronic overload relay - will be set to 160A
Cables to motor - looks like 16 or 25mmsq - in parallel from the contactors ie. 2 cables are connected to each motor.
The motor is only about 2m away from the switchgear.
Motor ratings - each is 90kW, 161A, 380V.
I'm trying to arrange a supply for this conveyor, but I'm limited to installing either a 250A or possibly 300A breaker at the point of supply. This will be OK, since the conveyor will not likely be running at full load.
Not being in possession of the Buff Book, is there any standard I can look up online to check whether the above arrangement is OK. I would actually like to recommend that the panel be re-wired, with the cable to each motor protected by it's own circuit breaker, but I will need to substantiate this. Presently the cable to each motor does not have any short circuit protection, but if the cable run is so short, will this then be acceptable?
Any comments on this arrangement will be appreciated.
Regards,
However, we've taken delivery of a feeder conveyor which uses a large circuit breaker to supply the two motors on the conveyor, with a contactor and overload relay for each motor.
The exact details of the circuitry are as follows:
Main incomer circuit breaker rating on the conveyor - 630A
Contactor rating 185A - 2 off connected in parallel for each motor.
Electronic overload relay - will be set to 160A
Cables to motor - looks like 16 or 25mmsq - in parallel from the contactors ie. 2 cables are connected to each motor.
The motor is only about 2m away from the switchgear.
Motor ratings - each is 90kW, 161A, 380V.
I'm trying to arrange a supply for this conveyor, but I'm limited to installing either a 250A or possibly 300A breaker at the point of supply. This will be OK, since the conveyor will not likely be running at full load.
Not being in possession of the Buff Book, is there any standard I can look up online to check whether the above arrangement is OK. I would actually like to recommend that the panel be re-wired, with the cable to each motor protected by it's own circuit breaker, but I will need to substantiate this. Presently the cable to each motor does not have any short circuit protection, but if the cable run is so short, will this then be acceptable?
Any comments on this arrangement will be appreciated.