interstructeng
Structural
- Jul 4, 2012
- 16
Hi, I'm working on a project involving the construction of a one story electrical room. The existing ground conditions are circa 1000mm of Made Ground (i.e. not suitable for supporting load) underlain by some clay that gets stiffer with depth. The Geotechnical report is giving me 25 kPa (so very low) capacity at the clay.
Structurally I'm looking at a 250mm RC slab designed to 7.5 kPa live load. So Dead Load circa 0.25*25 = 6.25, live load = 7.5 -> total SLS = 14 kPa so I am happy enough with that as a ground bearing slab.
I'm looking at a strip footing for the walls which is my concern. The max wall height is 4000mm (double leaf wall) with a concrete roof (no access) say 150mm thick. When I look at the line load from something like this it is very hard to get down to 25kPa with a strip footing.
I am going to get the made ground excavated out and replaced with compacted granular fill. Maybe I should be using a 45 degree spread through the granular fill (i.e. stone) in the calculation to spread it out a little more. I think I might be missing some consideration here - anyone have any thoughts?
It would seem strange to me to not be able to get a small structure like this to work on strip footings. I could thicken the whole slab to 300mm maybe as a raft? We don't have to consider frost heave heave due to the climate.
Structurally I'm looking at a 250mm RC slab designed to 7.5 kPa live load. So Dead Load circa 0.25*25 = 6.25, live load = 7.5 -> total SLS = 14 kPa so I am happy enough with that as a ground bearing slab.
I'm looking at a strip footing for the walls which is my concern. The max wall height is 4000mm (double leaf wall) with a concrete roof (no access) say 150mm thick. When I look at the line load from something like this it is very hard to get down to 25kPa with a strip footing.
I am going to get the made ground excavated out and replaced with compacted granular fill. Maybe I should be using a 45 degree spread through the granular fill (i.e. stone) in the calculation to spread it out a little more. I think I might be missing some consideration here - anyone have any thoughts?
It would seem strange to me to not be able to get a small structure like this to work on strip footings. I could thicken the whole slab to 300mm maybe as a raft? We don't have to consider frost heave heave due to the climate.