joejensen16
Electrical
- Jun 30, 2022
- 5
I have a large workshop in a residential neighborhood and when we built the utility installed 2 transformers to provide 600A of open delta 240V to the detached workshop. I've had a ton of problems. This is in Arizona and the utility is SRP. Late last spring I installed the first 3 phase machine which runs on a VFD. The VFD would constantly fault for input phase loss. In measuring the voltages that summer they were always spot on at 240.1V between all three phases. Oddly, on 4 different 3 phase machines the current on L2 (not the wild leg) was always low, some days 5% some days as much as 18%. This was on all machines. Not all the same drop but always L2 on all machines. I assumed that meant there was a phase problem. But when the utility installed a data logger it showed no phase problem. Phase perfect on all three legs, voltage the same on all three legs but on 4 different machines the current was always very low. This went on for months and in the end the utility kept a data logger running for months. By Sept the peak cooling loads for the city were dropping and the power was better. Fine all winter. Now this summer the VFD again faults out but this time the voltages are all over the place. They are close in the morning before peak loads and then the move apart in the temp outside climbs.
First, the single phase load on the workshop has never exceeded 50A and most of the time I took my own measurements I had all other breakers off.
I'm a BSEE but 38 years out of school and never a power engineer. The data from last year when the voltages were way off was:
L1-L2 = 240.1v
L2-L3 = 240.1v
L1-L3 = 240.1v
Current
L3 = A
L2 = 0.8 * A
L3 = 1.05 * A
Today for example (did not measure current)
L1-L2 = 246.5v
L2-L3 = 250.6v
L1-L3 = 242.6v
Is I have been unable to find any formulas of spreadsheets to help me understand how with open delta ungrounded I could get these measurements.
I suspect the Utility has a known issue a the main overhead line feeding our neighborhood and the underground in the neighborhood are scheduled for replacement in 2023 and they were installed in the early 1980s which I am told is not old by utility standards. The account manager and I am unable to get any info from the utility engineers. With the account manager I've been able to get 7 different calls with the utility engineers and each time they bring another expert in.
First, the single phase load on the workshop has never exceeded 50A and most of the time I took my own measurements I had all other breakers off.
I'm a BSEE but 38 years out of school and never a power engineer. The data from last year when the voltages were way off was:
L1-L2 = 240.1v
L2-L3 = 240.1v
L1-L3 = 240.1v
Current
L3 = A
L2 = 0.8 * A
L3 = 1.05 * A
Today for example (did not measure current)
L1-L2 = 246.5v
L2-L3 = 250.6v
L1-L3 = 242.6v
Is I have been unable to find any formulas of spreadsheets to help me understand how with open delta ungrounded I could get these measurements.
I suspect the Utility has a known issue a the main overhead line feeding our neighborhood and the underground in the neighborhood are scheduled for replacement in 2023 and they were installed in the early 1980s which I am told is not old by utility standards. The account manager and I am unable to get any info from the utility engineers. With the account manager I've been able to get 7 different calls with the utility engineers and each time they bring another expert in.