Hello all,
My first post here, so if I leave anything out let me know. I am dealing with a utility that is demanding we install wye-wye pts for protective relaying in our gear. We are connecting to the utlity with 5 2.2MW gens at 13.2kV. We have capacity for up to 12. The system will be paralleled for several minutes but will never export power.
The utility is demanding the y-y PT because of a requirement in IEEE 1547. Their argument is that if a phase upstream of my facility (on their grid) goes to ground and the gens are online the y-y pt is required to capture a voltage sag due to the ground fault. The protective relay is a GE750. I get the sense they are demanding this only because its in 1547, they can't explain to me why the y-y is superior in this instance to the open delta.
My questions
1) Is there any advantage of the y-y over the open delta?
2) Looking for a voltage drop to clear a ground fault seems like a rather round about way of clearing a ground fault. Wouldn't is just be better to use the 51g setting in the relay to clear the ground fault? Or possibly the residual ground fault settings?
My first post here, so if I leave anything out let me know. I am dealing with a utility that is demanding we install wye-wye pts for protective relaying in our gear. We are connecting to the utlity with 5 2.2MW gens at 13.2kV. We have capacity for up to 12. The system will be paralleled for several minutes but will never export power.
The utility is demanding the y-y PT because of a requirement in IEEE 1547. Their argument is that if a phase upstream of my facility (on their grid) goes to ground and the gens are online the y-y pt is required to capture a voltage sag due to the ground fault. The protective relay is a GE750. I get the sense they are demanding this only because its in 1547, they can't explain to me why the y-y is superior in this instance to the open delta.
My questions
1) Is there any advantage of the y-y over the open delta?
2) Looking for a voltage drop to clear a ground fault seems like a rather round about way of clearing a ground fault. Wouldn't is just be better to use the 51g setting in the relay to clear the ground fault? Or possibly the residual ground fault settings?