Why does an open delta provide 58% power instead of 2/3 the power of a regular delta?
 
Replies continue below

Recommended for you

Think about what the difference is between the open delta xfmr, and it's line currents compared to what the "delta currents" would be. Then compare that to a regular delta. A standard delta's line currents differ by root 3 of the "delta currents". Make sense?

Mike
 
What I know about open delta is:

I-phase = I-line

V-phase = V-line

For regular delta:

1.73*I-phase = I-line

V-phase = V-line

Is this correct?
 
In a Closed Delta the line current is shared by two windings.
When used in Open Delta, the transformers must be derated 86.6% to avoid overloading. After you have derated the transformers 86.6% you multiply by 2/3.

Look at it another way;
One 33 Kva transformer = 33 KVA
Two 33 1/3 Kva transformers, derated for open delta service.
66 2/3 Kva x 86.6% = 57.7 Kva
Three 33 1/3 Kva transformers = 100 Kva.
 
In an open-delta (V) connection, the line current is limited to the phase current of Iline/[√]3 to avoid transformer overload. The maximum power available is:

a) Two transformer (Open Delta): PV=[√]3Elinex Iline/[√]3 = Elinex Iline.

b) Three transformer (Closed Delta): P[Δ]=[√]3Elinex Iline .
PV/ P[Δ]= 1/[√]3= 57.7%

 
thanks everyone... I also found a great reference in the book "Principles of Electric Machines and Power Electronics" pg.75-78. It's all about those sneaky phase shifts. [thumbsup2]
 
You should give Cuky a star for the answer. I suggest you draw out the circuit and work it out long-hand. If you assume a voltage of 1<0, 1<-120 and 1<120 and impedances of 1<0, you can easily determine what the power is on an open delta system. Then use the simple 3 phase power equation for a closed delta system. You'll then find the ratio Cuky gave you.