I have an opening (36" x 36") at the edge of the slab (concrete over metal deck). The beam that is spanning between the joists according to me should take the point load from the edge angle only since the deck spans from joist to joist. One of the engineers in the office, says it should take the entire load from wall to wall [load = 20'/2 * (dl+ ll)]. Is that correct?

What is load on the beam at the opening?
 
 http://files.engineering.com/getfile.aspx?folder=925cdc17-2bc4-4279-82ff-5129ea16d6b2&file=question.pdf
Replies continue below

Recommended for you

I agree with you on the assumption that the deck spans one way in this location. In reality you will get some two way spanning happening, but I find it hard to imagine how you would need to take the full tributary distance wall to wall.

Worse case if there is some two way spanning happening then it would be close to a triangular UDL with a tributary width of half the trimming beam span on the trimming beam (+ point load from the trimming angle).
 
@Kotor: I agree with you. Your colleague appears to be horribly mistaken regarding what is supporting what in this situation. Perhaps you misunderstood his or her intent.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 