Bob1680
Structural
- Mar 24, 2022
- 6
Hello, Guys,
Does an 10ft opening on non-loadbearing ICF wall require a lintel with stirrup like a concrete beam or just a rebar ?
By the following Ontario building code, it seems just a rebar reinforcing. However, on ICF manufacture's manual, Lintel tables do not show that it is for loadbearing walls( See the Attachment.
9.20.17.3. Openings in Non-Loadbearing
Flat Insulating Concrete Form Walls
(1) No openings shall occur within 1.2 m of interior and
exterior corners of exterior non-loadbearing flat insulating
concrete form walls.
(2) Portions of walls over openings in non-loadbearing
flat insulating concrete form walls shall have a minimum
depth of concrete of not less than 200 mm over the width of
the opening.
(3) Openings more than 600 mm but not more than 3 m
in width in non-loadbearing flat insulating concrete form
walls shall be reinforced at the top and bottom with one
10M bar.
(4) Openings more than 3 m in width in non-
loadbearing flat insulating concrete form walls shall be
reinforced on all four sides with two 10M bars.
(5) Reinforcing bars described in Sentences (3) and (4)
shall extend not less than 600 mm beyond the edges of the
opening.
Thanks,
Does an 10ft opening on non-loadbearing ICF wall require a lintel with stirrup like a concrete beam or just a rebar ?
By the following Ontario building code, it seems just a rebar reinforcing. However, on ICF manufacture's manual, Lintel tables do not show that it is for loadbearing walls( See the Attachment.
9.20.17.3. Openings in Non-Loadbearing
Flat Insulating Concrete Form Walls
(1) No openings shall occur within 1.2 m of interior and
exterior corners of exterior non-loadbearing flat insulating
concrete form walls.
(2) Portions of walls over openings in non-loadbearing
flat insulating concrete form walls shall have a minimum
depth of concrete of not less than 200 mm over the width of
the opening.
(3) Openings more than 600 mm but not more than 3 m
in width in non-loadbearing flat insulating concrete form
walls shall be reinforced at the top and bottom with one
10M bar.
(4) Openings more than 3 m in width in non-
loadbearing flat insulating concrete form walls shall be
reinforced on all four sides with two 10M bars.
(5) Reinforcing bars described in Sentences (3) and (4)
shall extend not less than 600 mm beyond the edges of the
opening.
Thanks,