tumbleweed1
Electrical
- Sep 19, 2013
- 44
We have a 1500A utility feeder with 1500:5A protection CTs. We are connecting internal generation that will displace the utility power, but not export power to the utility. We will maintain a minimum import, and when we do, we can have as little as 20A incoming from the utility.
For the purpose of reverse power protection, we would like to set a trip such that if we fall less than our desired minimum import, that we will trip off. This will be our "buffer" from exporting.
My concern is operating on the low end of the CT primary rated current. Can we expect large inaccuracies in current measurement? Are there some CT ratings that would be better to use than others? We also have an estimated length of 400ft of 10awg copper to connect the CTs to the relay.
How can I determine an adequate CT selection for this application?
For the purpose of reverse power protection, we would like to set a trip such that if we fall less than our desired minimum import, that we will trip off. This will be our "buffer" from exporting.
My concern is operating on the low end of the CT primary rated current. Can we expect large inaccuracies in current measurement? Are there some CT ratings that would be better to use than others? We also have an estimated length of 400ft of 10awg copper to connect the CTs to the relay.
How can I determine an adequate CT selection for this application?