RAgrawal
Electrical
- Aug 31, 2001
- 59
There is a small about 10 MW, 3000 RPM Generator coupled to a back pressure Turbine in our plant. One day, Excitation of the generator failed along with station DC power failure (supplied by 220 DC battery bank). Due to failure of DC power, no relay could the detect the loss of field / trip the generator. Even operation people could not trip the generator, as there was no DC power for that particular machine.
Since system was strong enough to supply the increased reactive power demand, there was no other disturbance in system e.g. voltage dip etc. After 8 minutes, machine copuld be isolated by tripping upstream breaker. Tripping of machine caused the over speeding of Turbine but this whole incidence caused the tremendous damage to the Generator. Its rotor was flied off towards Turbine by breaking the coupling and shaft by about a meter. Fire also taken place in the plant. Machine was operating at full load even after the loss of excitation.
Can any one comment on this incident and have any idea about the capacity of machine to operate as Induction Generator? Trends of system parameters are available, if any one of you is interested.
Since system was strong enough to supply the increased reactive power demand, there was no other disturbance in system e.g. voltage dip etc. After 8 minutes, machine copuld be isolated by tripping upstream breaker. Tripping of machine caused the over speeding of Turbine but this whole incidence caused the tremendous damage to the Generator. Its rotor was flied off towards Turbine by breaking the coupling and shaft by about a meter. Fire also taken place in the plant. Machine was operating at full load even after the loss of excitation.
Can any one comment on this incident and have any idea about the capacity of machine to operate as Induction Generator? Trends of system parameters are available, if any one of you is interested.